
15
69-1431–1
The minimum off-timer operates in cooling on
the T8000 and T8001, T8002, T8024 (multi-
stage model) and in first stage heating or
cooling on the T8011 (heat pump model). A
flashing flame or snowflake indicates the
minimum off-time is in effect.
Minimum Off-Timing
The thermostat minimum off-timer assures that
the compressor does not come on again for at
least five minutes after it turns off. The minimum
off-timer is triggered when the compressor turns
off and when the SYSTEM switch position is
changed. If the compressor turns off when the
setpoint is changed, the minimum off-timer is
triggered. Power interruption and power
restoration also trigger the minimum off-timer.